Upsize Wire Size

Status
Not open for further replies.

mstrlucky74

Senior Member
Location
NJ
Just not clear on how this makes sense. Currently have abdHLP panel with existing 15,20a loads…very fee 30a loads. These loads will nowbe feed from a new HLP panel in a building about 300’ away. SO they want us tointercepts these branch circuits and run them to the new panel. A few questions.

If these currently small loads that are close to theexisting panel I’m sure they are #12’ and #10’s for the 15 &20A loads. Howthe heck could we splice to #4’s from #10’s or 12’s.? I understand they seem towant this for voltage drop and derating but the upsize seems like a lot.
So..
1. Could you splice from #12’s to #4’s? What would you landthe wire on before landing on the panel breaker as you can’t terminate #4’s ona 20a breaker?
2. The upsizing seems awful large for these loads, which we don’tknow what they are.
 

Attachments

  • Capture.jpg
    Capture.jpg
    33.4 KB · Views: 0
  • Capture 2.jpg
    Capture 2.jpg
    38.4 KB · Views: 0

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Use Polaris style connectors. All of your EGC's are too small.

Z_sKxyqcpEx_.JPG
 
Status
Not open for further replies.
Top