scotteng
Member
- Location
- Apollo Beach, FL
- Occupation
- Professional Engineer
I have a client that has a tenant lease agreement requesting a #1/0 Cu EGC to be run for their 400A tenant service. Table 250.122 only requires a #3 Cu EGC of course. And we are all familiar with the requirement to upsize the EGC when the phase conductors are upsized for VD. But is there anything specific in the code that prohibits someone from increasing the EGC to any arbitrary size just because they want to? Here they are asking for a #1/0, but could we run a #4/0 CU EGC on a 400A service? Never been asked to upsize the EGC before and cannot find anything that says you can't.