onelectrishun
Member
Please excuse my ignorance on this issue. I probably should know what the answer is from my apprenticeship days back in the 70?s?
We?re feeding a 1Ph, 120/240V, 200A sub panel from a source 1500 ft. away. The wire has to be upsized to 1250 kcmil conductors to compensate for voltage drop over that distance. (I did some quick voltage drop calcs on different calculators on line and came up with varying results, so let?s just assume the 1250 kcmil is correct for now. Let?s say that we set a junction box every 250? along this run.
So?could we run 1250 kcmil for the first 250 ft., a smaller conductor, say 900 kcmil for the next 250 ft., 750 kcmil for the 3rd 250? and so on. The smallest conductor(s) would be 4/0?s for the sake of discussion.
Depending on the answer to my quandary this brings up other questions like:
If so, how do you figure the size of wire at each segment of the run?
If not, how does the above example differ from a distribution system?say you run from a 1200A DB to a 600A DB with 2-350?s, then from the 600A DB to a 400A DB with 2-3/0?s, then from the 400A DB to a 200A PB with a 3/0, etc. Assume no other loads on any of these panels. Isn?t that exactly the same thing in theory?
We?re feeding a 1Ph, 120/240V, 200A sub panel from a source 1500 ft. away. The wire has to be upsized to 1250 kcmil conductors to compensate for voltage drop over that distance. (I did some quick voltage drop calcs on different calculators on line and came up with varying results, so let?s just assume the 1250 kcmil is correct for now. Let?s say that we set a junction box every 250? along this run.
So?could we run 1250 kcmil for the first 250 ft., a smaller conductor, say 900 kcmil for the next 250 ft., 750 kcmil for the 3rd 250? and so on. The smallest conductor(s) would be 4/0?s for the sake of discussion.
Depending on the answer to my quandary this brings up other questions like:
If so, how do you figure the size of wire at each segment of the run?
If not, how does the above example differ from a distribution system?say you run from a 1200A DB to a 600A DB with 2-350?s, then from the 600A DB to a 400A DB with 2-3/0?s, then from the 400A DB to a 200A PB with a 3/0, etc. Assume no other loads on any of these panels. Isn?t that exactly the same thing in theory?