A plan shows a 100 amp 480V breaker feeding two conductors that are upsized from #3 to 350MCM
for voltage drop. The plans call for a #4 grounding conductor with the 350's. I'm calculating something different.
#350 MCM 350,000CM Upsized conductor
#3 52,560CM 100 amp conductor
#8 16,510CM ground
350,000/52,560*16,510 = 109.941CM
#1/0 105,600CM
#2/0 133,100CM
Do I need to use a 2/0 for this run? Seems huge so I'm wondering if I'm doing the calculation incorrectly.