PSU Electrical
Member
- Location
- Bethlehem/Scranton
I have a 400A, 480V Main Distribution Panel located on a platform near a river where power is feed from another location about 1200' away. (Getting the utility to provide a 3-phase service near the river would have taken forever). So, we have extended a feeder about 1200' away to this 400A panel; load on the panel is about 220A. Typically from a 400A breaker, I would run 500MCM with a #3 EGC. To compensate for voltage drop, I ran parallel 500MCM with #3EGC in two separate conduits. The inspector is telling me the EGC needs to be larger per 250.122(B). Now I understand what he is bringing up about proportionally increasing the EGC, but my thought behind this is 500MCM (500,000mils) and #3 (52,620 mils) so if I add a second 500MCM run (1,000,000mils of ungrounded conductor) and I include a 2nd EGC in the other conduit that would give me a total of 105,240 mils of EGC (total for the circuit). If I add a second 500MCM to compensate for voltage drop as I did, does the EGC in EACH conduit need to be upsized??? I think he is telling me I would need to proportionally increase the EGC in each (go with 1/0). I'm confused b/c they are separate conduits.