Upsizing feeder wire and GND for voltage drop

Merry Christmas

PanelGuy1315

Member
Location
Louisville
Occupation
Electrical Designer
I need help from wire sizing gurus. I've had this same question come up multiple times when designing a feeder to control panel.

Say a large MCP needs a 400A feed from a distribution panel 1000' away (distance inflated to make point). Without taking voltage drop into account we would typically size the feed to 2 sets of 3/0 with a #3 GND in each conduit.

When I adjust feeder wire size to keep voltage drop below 3%, I come up with 2 sets of 600kcmil. I also have read that I need to increase GND wire size by the same ratio as I increased the feeder wires.

How would you do this with the parallel feed? I went from 3/0 to 600kcmil, which I calculate as a 3.57 factor increase (by cir mils). Do I increase the #3 GND in each conduit by 3.57 factor? I'm coming up with needing a GND wire with 188,152 cirmils which would be a 4/0 wire.

Thanks for your input.
 

PanelGuy1315

Member
Location
Louisville
Occupation
Electrical Designer
In parallel conduits, each EGC basically needs to be sized as if it was the only one for the entire feeder.
Right, and that's what I have with the #3 EGC (sized for the 400A overcurrent protection) in each parallel conduit. But I also feel I need to upsize that #3 because I am upsizing the feeder conductors for voltage drop.
 