I recently ran a 120/208V,1Ph power feed to a panelboard across a parking lot. The distance of the run caused me to have to upsize the phase conductors from #4 to #4/0. Unfortunately I forgot to upsize the ground conductor proportionately to the upsizing of the phase conductors as indicated in NEC 250.122. This would have changed my #8 ground conductor to a #1 ground conductor.
My question is can I expect to have grounding issues due to the undersized ground, and if so can the ground wire be supplemented with a ground rod at the location of the panelboard?
My question is can I expect to have grounding issues due to the undersized ground, and if so can the ground wire be supplemented with a ground rod at the location of the panelboard?