hitehm
Senior Member
- Location
- Las Vegas NV
We have a 150A main breaker panel that we need to install as a subpanel to land our solar breaker. Assume for now we can't find a lower amp main for the subpanel and the subpanel is on a separate building and requires a disconnect so it can't be MLO. The feeder breaker upstream in the main panel feeding this subpanel is 100A. So we will basically have a 100A main feeding a 150A main in the subpanel. Obviously, the 100A main breaker being upstream will limit the current to 100A. So as far as the 120% rule, can it be said that the breaker protecting the bus is 100A and the 150A breaker in the sub is acting solely as a disconnect and not as the bus OCPD?