Code requires wires serving a motor to be sized at 125% of FLA, while the breaker can be much larger. I typically use 200% of FLA to size a breaker for a motor. The wiring is protected from overload by the motor's overload protection rather than the breaker which provides short circuit protection. To me it seems logical that the disconnect should be sized the same as the wire (i.e., 125% of FLA). Is that correct, and if so where does code clarify this? Sorry, I'm on vacation and don't have my code book. For instance:
If motor FLA: 45A
125% = 56A, so a 60A non-fused disconnect is OK.
200% = 90A, so a 90A or 100A breaker could be used. Would a 100A breaker adequately protect the 60A disconnect?
If motor FLA: 45A
125% = 56A, so a 60A non-fused disconnect is OK.
200% = 90A, so a 90A or 100A breaker could be used. Would a 100A breaker adequately protect the 60A disconnect?