mddorogi
Member
- Location
- Ann Arbor, MI
I've seen URD quadruplex wire and wanted to use it for underground AC runs. See attached below. There are a couple points I am confused about and having a tough time figuring it out. I have an AC run from PV AC combiner panel to 480/208 transformer at 230' long. The current is 180.55A, and including 1.25 factor that's 225.7A.
Using NEC table 310.15(B)(16), I'd use 300 mcm aluminum with ampacity of 230A. Voltage drop is less than 2%. There is no quadruplex wire using 300 mcm, but there is "slippery rock" using 350 mcm. It lists an direct bury ampacity of a whopping 385A. I called to ask where that number comes from and didn't get an answer. I have two questions:
- is URD wire NEC approved? Has anyone used it for underground AC runs in solar installations?
- how would they get a direct bury ampacity of 385A for 350 mcm aluminum wire?
Using NEC table 310.15(B)(16), I'd use 300 mcm aluminum with ampacity of 230A. Voltage drop is less than 2%. There is no quadruplex wire using 300 mcm, but there is "slippery rock" using 350 mcm. It lists an direct bury ampacity of a whopping 385A. I called to ask where that number comes from and didn't get an answer. I have two questions:
- is URD wire NEC approved? Has anyone used it for underground AC runs in solar installations?
- how would they get a direct bury ampacity of 385A for 350 mcm aluminum wire?