24 CFR Part 3280
3280.803
Power supply.
(2) An approved raceway from the disconnecting means in the
manufactured home to the underside of the manufactured home with
provisions for the attachment of a suitable junction box or fitting to
the raceway on the underside of the manufactured home. The manufacturer
shall provide in his written installation instructions, the proper
feeder conductor sizes for the raceway and the size of the junction box
to be used;
3280.808
Wiring methods and materials.
(k) When outdoor or under-chassis line-voltage wiring is exposed to
moisture or physical damage, it shall be protected by rigid metal
conduit. The conductors shall be suitable for wet locations. Electrical
metallic tubing may be used when closely routed against frames, and
equipment enclosures.
(l) The cables or conductors shall be Type NMC, TW, or equivalent.