Hello,
We have a restaurant and a high temperature double deck pizza oven out of the UK, made in Sweden.
Each deck is rated for european 3 phase 400v, uses 18.5 amps on each oven, 12.6 kw power each oven, 25.2 kw total.
The power in the building is an older 240v 3 phase delta with a high b leg.
We believe a 25 kva transformer would max it out and need to add a 20% cushion putting it just over 30 kva
and need to step up to a 45 kva.
We believe we need a 45 kva delta to wye transformer with neutral on wye side + ground going to the oven with
separate cut off switches with 20 amp fuses from the transformer.
We also believe we need a breaker over 65 amps in the supply breaker panel to feed the transformer.
Can we get a second opinion? do you concur?
Thanks for your input,
Mike