It all depends on what you end up with after doing a derating calculation. Picking numbers (like no more than 4 or 8) out of the air will accomplish nothing. And yes heat is the issue with bundling cables together.

Welcome to the forum.
 
The exception in 310,15(B) might give some insight:
Exception No. 5: Adjustment factors shall not apply to Type AC cable or to Type MC cable without an overall outer jacket under the following conditions:
(1) Each cable has not more than three current-carrying conductors.
(2) The conductors are 12 AWG copper.
(3) Not more than 20 current-carrying conductors are bundled, stacked, or supported on ?bridle rings.?
A 60 percent adjustment factor shall be applied where the current-carrying conductors in these cables that are stacked or bundled longer than 600 mm (24 in.) without maintaining spacing exceeds 20.
 
The exception in 310,15(B) might give some insight:
Exception No. 5: Adjustment factors shall not apply to Type AC cable or to Type MC cable without an overall outer jacket under the following conditions:
(1) Each cable has not more than three current-carrying conductors.
(2) The conductors are 12 AWG copper.
(3) Not more than 20 current-carrying conductors are bundled, stacked, or supported on ?bridle rings.?
A 60 percent adjustment factor shall be applied where the current-carrying conductors in these cables that are stacked or bundled longer than 600 mm (24 in.) without maintaining spacing exceeds 20.

Yup, that exception is very handy when running #12 AWG MC cable, however he's asking about #10 AWG. :)
 
I'm still learning to read :)
silly little details they slip in there.
 