jerrystull
New member
- Location
- Strasburg, Virginia
How many "tightly" bundled 10/2 MC cables can be safely together? I asked for no more than 8, The JHA designer said up to 4" in one bundel. Does heat build up mean anything?
The exception in 310,15(B) might give some insight:
Exception No. 5: Adjustment factors shall not apply to Type AC cable or to Type MC cable without an overall outer jacket under the following conditions:
(1) Each cable has not more than three current-carrying conductors.
(2) The conductors are 12 AWG copper.
(3) Not more than 20 current-carrying conductors are bundled, stacked, or supported on ?bridle rings.?
A 60 percent adjustment factor shall be applied where the current-carrying conductors in these cables that are stacked or bundled longer than 600 mm (24 in.) without maintaining spacing exceeds 20.