Usage Monitor Installation
Nobody900
Los Angeles
Electrical Engineer
I am an electrical engineer, not an electrician. I live in California. I am installing an Emporia Vue 2 in my service entrance panel to try to figure out why my electricity bill is routinely $800 a month as Edison is no help in trying to diagnose usage. The installation requires connecting to a breaker on each leg of 120v power, and another wire to the neutral bus. In my panel the very few empty neutral bus locations are difficult to access, while there are many easily accessible ground bus locations. My expectation is that since this is the entrance panel, ground and neutral are bonded together at the panel, but I have not personally verified that. My question is, is it acceptable to connect to the ground bus for this application or do I have to go digging through the wiring in the panel to access a neutral? Emporia told me this is OK, but I am not sure I trust their knowledge of code requirements so I am asking experts.
Also, given the way the device is installed, it seemed possible that an internal failure could result in both 120v legs of the incoming service getting shorted together, albeit each leg protected by a breaker. I asked Emporia about this and they responded that while that failure couldn't be ruled out, they had no reports of this occurring. Any thoughts on what the consequences of that failure might be? Thanks in advance.
If this is your main service it is likely bonded there but could be in a disconnect outside as well. If it is the bonding location someone likely could have separated the grounds and neutrals incase it were to become a sub panel in the future like most people suggest in this forum.
If the ground bus is mounted to the can, and the neutral bus is bonded to the can with a screw, you cannot use the ground bus to land the neutral. That results in neutral current being conducted by the enclosure.
In most cases, if your main breaker is located in the panel, it's your first point of disconnect. To verify, look for a green bonding screw connecting the neutral bar to the metal enclosure or a pre-formed metal bar connecting the neutral bar to the metal enclosure.