- Location
- Chapel Hill, NC
- Occupation
- Retired Electrical Contractor
We are discussing this on another forum and I know we have discusses it here. The results on this forum was that if it is USE-2 and marked as Rhw or Thwn etc then it can be run in conduit inside. I am OK with that however how do we get around section 338.12(B)
The poster at the other forum got rejected and quite frankly I don't know if he has a leg to stand on. The code says NO for indoors and does not mention USE-2. USE-2 is still USE cable....Why have we been telling people it is okay?
My take on it is that we can use USE-2 as an UG cable without conduit or we can use the cable as Rhw-2 or whatever it is marked and thus it isn't USE cable anymore.... That is strange if that is the case.
Any comments
The poster at the other forum got rejected and quite frankly I don't know if he has a leg to stand on. The code says NO for indoors and does not mention USE-2. USE-2 is still USE cable....Why have we been telling people it is okay?
My take on it is that we can use USE-2 as an UG cable without conduit or we can use the cable as Rhw-2 or whatever it is marked and thus it isn't USE cable anymore.... That is strange if that is the case.
Any comments
(B) Underground Service-Entrance Cable. Underground
service-entrance cable (USE) shall not be used under the
following conditions or in the following locations:
(1) For interior wiring
(2) For aboveground installations except where USE cable
emerges from the ground and is terminated in an enclosure
at an outdoor location and the cable is protected in
accordance with 300.5(D)
(3) As aerial cable unless it is a multiconductor cable identified
for use aboveground and installed as messenger supported
wiring in accordance with 225.10 and Part II of
Article 396