Thank you for the additional information. Because of its criticality, I would take NFPA 72 Chapter 21, NFPA 90A, 92 and 101 into consideration. It makes a difference whether this is a stand-alone system, part of a supervisory system, AHU with smoke detectors etc. because I would question whether this should be an automatic shut off etc. It is important to understand the requirements
As it is mentioned, I have used RIB relays which are controlled by duct smoke detectors "dry contacts" as part of the emergency stop circuit. Turning off the control signal to motor's VFD, magnetic starter etc.
For example: 6.4.3.1 Smoke detectors provided as required by 6.4.2 shall automatically stop their respective
fan(s) on detecting the presence of smoke.
"Where duct smoke detectors are installed to shut down associated HVAC air-handling units and
the building does not contain a fire alarm and signaling system, 6.4.4.3 of NFPA 90A requires that duct
smoke detector activation cause a visual signal and an audible signal in a normally occupied area, and
that duct smoke detector trouble conditions be indicated visually or audibly in a normally occupied
area and identified as air duct detector trouble."
If you are not using smoke detectors and the manual control to shut down the fans is "approved" by authorities, I would go with what
@hillbilly1 suggested.