I'm running a 100A feeder to a remote garage and would like to use aluminum USE direct burial cable. My background is manufacturing, so I don't have a lot of experience with this direct burial stuff... This is for a friend who has an existing manufactured home with a combo meter/panel on a pole and he is adding a small garage approximately 100ft away. I was planning to run copper in PVC from this panel, 18" deep and stub up directly into the main breaker panel inside his new building, but less expensive alternative is to run 2-2-2-4 Southwire aluminum at 24" and only use schedule 80 at each end (see wire specs and link below). I can buy the wire by the foot from Home Depot.
My question is about 338.12 (B) (USE uses not permitted). It sounds like USE cannot be run indoors and must be terminated in an enclosure located outdoors. I haven't examined hundreds of residential panels, but it seems like I've seen USE connected to several main breakers in the past. Is it because it's usually rated RHH and RHW...???
Probably a silly question, but I just wanted to make sure.. The building department is making my friend add a footer to his small building, so I'm telling him to go ahead and install the stub up before he pours the additional concrete. I assume the new footer will extend away from the building, so I wouldn't want to have to come back and put in an external J-box.
Thanks for your comments...
2-2-2-4 : 2awg hot - 2awg hot - 2awg Neutral - 4awg ground
https://www.southwire.com/ProductCatalog/XTEInterfaceServlet?contentKey=prodcatsheet15
Construction:
Southwire® mobile home feeder consists of four quadruplexed type RHH or RHW-2 or USE-2 Alumaflex® Brand AA-8000 series aluminum alloy compacted conductors. The cable contains 2 triple-extruded phase conductors, a white striped neutral conductor and a green grounding conductor to eliminate the need for field marking per the National Electrical Code. The insulation is sunlight resistant.
Construction: