Use Main Breaker or Backfeed on Subpanel?

Status
Not open for further replies.
I've got a detached garage/shop in the process of being powered from the house 200A main breaker panel using 4 wires in buried conduit. My electrician determined that his #2 Aluminum XHHW feeder be protected by an 80A breaker at the main panel. The wire length is about 140 feet. He installed a 8 circuit subpanel in the detached garage and used an 80A backfed breaker on the incoming feed, matching the breaker amperage at the main panel.

As the garage was wired, it turns out we needed at least 16 circuits (due to stuff I added), so we decided to replace the small panel with a 24/24 circuit Siemens panel which I purchased. (My electrician's supplier doesn't carry Siemens, and since the house has a Siemens main panel, I wanted to match brands and breakers.) The Siemens panel came with a 100A main breaker.

My electrician says he will need to remove the 100A main breaker, and asked me to get a 80A breaker to backfeed the subpanel. He refuses to install the new panel until I do so.

Why? Isn't the 80A feeder breaker in the house panel already protecting the feeder wires? Doesn't the 100A main breaker on the new subpanel just serve as a disconnect?

He claims that "there is no way" the 80A feeder breaker at the main panel would trip in time to protect the 140 feet of wire from the main to the subpanel, if for some reason the full 100A was attempted to be drawn at the subpanel.

The retired electrician at the hardware store insists otherwise- that as long as the feeder wires are protected by the 80A breaker on the main panel, the size of the main breaker on the subpanel does not also have to be 80A.

A permit has been pulled, and it will be inspected. I want to be completely code-compliant, and do not want to "cut corners". My electrician says without the 80A incoming breaker on the subpanel, we won't pass, and he will not subject himself to the embarrassment.

I really don't have a problem with using a backfed breaker, since we have the panel space. I prefer the "main breaker" type layout though. Is there any other good reason to use a "main breaker" type set-up instead of a back-feed?

Who's right in this case- the retired electrician who sold me the panel, or my electrician, who won't budge (rightly so, if he is correct, or even just being prudent), as he says the code does not allow it, "as by the definition of a protective device, the subpanel breaker will not be acting as a protective device for the incoming feeder".

By the way, despite being a retired electrical engineer, I have come to respect the experience and knowledge needed to correctly wire residential service. There has been a several month long process now of adding service and correcting the many "do-it-yourselfer" errors in my recently purchased home's wiring. I am happy to pay for my electrician's services, well worth it! This subpanel issue just has me curious, though.

[ November 13, 2005, 06:00 AM: Message edited by: lcdeyes ]
 
Re: Use Main Breaker or Backfeed on Subpanel?

Originally posted by lcdeyes:

He claims that "there is no way" the 80A feeder breaker at the main panel would trip in time to protect the 140 feet of wire from the main to the subpanel, if for some reason the full 100A was attempted to be drawn at the subpanel.
I would ask your electrician to quote the NEC section that prohibits this installation. The conductors are in fact protected by the 80 amp CB at the main panel. The above quote puzzles me. Is he saying that if you placed a non-fused disconnect and MLO sub-panel at the garage that the conductors would not be protected or that it would not be legal?

Just my opinion.

Mark
 
Re: Use Main Breaker or Backfeed on Subpanel?

Your electrician is incorrect.

The 100 amp breaker at the garage panel will not change the how the 80 amp breaker at the main panel operates.

Basically the 100 amp breaker at the garage will just be a means of disconnect which is fine.

As a side note, 2 AWG AL XHHW is rated 90 amps, the 80 amp breaker at the main panel could be bumped up to a 90 amp if you would like to.
 
Re: Use Main Breaker or Backfeed on Subpanel?

Bob,

I got 75 amps for #2 Aluminum @ 60 deg. Did I read the wrong line of the table. It looks like you may have used the 75 deg. column. Not knowing the termination temps, I think 60 deg. is appropriate for less than 100 amps.

Mark

[ November 13, 2005, 07:04 AM: Message edited by: busman ]
 
Re: Use Main Breaker or Backfeed on Subpanel?

I think you will be hard pressed to find any terminations on breakers or panelboards that are not rated 75C regardless of them being under 100 amps. :)

110.14(C)(1) Equipment Provisions. The determination of termination provisions of equipment shall be based on 110.14(C)(1)(a) or (C)(1)(b). Unless the equipment is listed and marked otherwise,.......
 
Re: Use Main Breaker or Backfeed on Subpanel?

lcdeyes, he's either mistaken or probably just a little unwilling to do it because it's sort of cheesy, not to mention he already installed the panel you asked for once, and no electrician likes to tear apart work they just did. (Has nothing to do with being paid for it or not) ...suddenly you're making changes & supplying your own equiptment in the middle of the job...The wires may be too short now...he has purchased an 80 amp breaker that is now worthless...

You are probably annoying the hell out of him! I know I would be pissed off!
Now on top of that you're going to go back to him and say, "The guys on the internet say You're wrong!"
Don't be surprised if he doesn't show up again.

Do him a favor, go buy a Siemens Breaker and retaining clip! OR buy a sub-panel to match the existing breaker he all ready has. Give the guy a break! ;)

Dave
 
Re: Use Main Breaker or Backfeed on Subpanel?

Originally posted by davedottcom:
or probably just a little unwilling to do it because it's sort of cheesy,
It is?

Why is it Cheesy?

You are probably annoying the hell out of him! I know I would be pissed off!
About what? A change made in the job.

This happens every day.


Do him a favor, go buy a Siemens Breaker and retaining clip! OR buy a sub-panel to match the existing breaker he all ready has. Give the guy a break!
Why should he 'give the guy a break' I am sure he is paying this EC and probably paid for change from one panel to the other.

Why should he pay for a breaker and clip that is unneeded?

I am totally surprised by your view here. :(

[ November 13, 2005, 09:49 AM: Message edited by: iwire ]
 
Re: Use Main Breaker or Backfeed on Subpanel?

Iwire,

What I meant was that if the circuit were rated over 100 amps, then the 75 deg. ampacity could be used. Without knowing the terminations, the 60 is the only sure bet. I agree that MOST CB's are 60/75 rated.

Mark

[ November 13, 2005, 09:55 AM: Message edited by: busman ]
 
Re: Use Main Breaker or Backfeed on Subpanel?

Originally posted by busman:
Iwire,

What I meant was that if the circuit were rated over 100 amps, then the 75 deg. ampacity could be used.

Mark
Mark you can use the 75 deg. ampacity on circuits under 100 amps if the terminations are rated 75 C and most are even on a 20 amp breaker.

Bob
 
Re: Use Main Breaker or Backfeed on Subpanel?

Iwire,

Sorry. I was editing while you were posting. I agree. I only meant that without knowing the terminations, the 60 degree is the only sure answer. Thanks for the catch.

Mark
 
Re: Use Main Breaker or Backfeed on Subpanel?

Originally posted by busman:
I only meant that without knowing the terminations, the 60 degree is the only sure answer.
I see. :)

I agree if put on 'the stand' or while taking a test I could not say all breakers are 75 C rated.

However have you any, or seen any recently purchased two pole 80s or 90s that are not rated 75 C? :cool:
 
Re: Use Main Breaker or Backfeed on Subpanel?

Dave, if this will help this EC better his knowledge, (even if reluctantly) and save the custmer some money, I would think it would be best to say "The guys on the internet say You're wrong!" :D

Roger
 
Re: Use Main Breaker or Backfeed on Subpanel?

Remember that;
240.21 Location in Circuit.
Overcurrent protection shall be provided in each ungrounded circuit conductor and shall be located at the point where the conductors receive their supply except as specified in 240.21(A) through (G).
This is not a tap so the breaker in the main panel is what protects the feeder conductors.
The 100 amp is only a disconnecting means as outlined in 225.

Stand your ground with this electrician. If he will not finish the work contact the inspection department and ask them for relief.
 
Re: Use Main Breaker or Backfeed on Subpanel?

Don't get me wrong the Electrician is incorrect.
There is no such code article

Why is it cheesy?
Just my opinion.
Hey, some of you thought my idea on how to back Feed a 120 Volt panel was Cheesy!

It was compliant, but cheesy none the less.

I guess Cheese is in the eye of the beholder! :D

"About what? A change made in the job. That happens every day"

True. It's just very annoying when people don't know what they want until after the work is completed. This always seems to happen on those jobs that the owner is on the site a lot! Next thing you know it's scewing up my schedule, and it starts effecting other jobs.
I was picturing myself...stressed out as it is...then after I complete the work, it all needs to be ripped out. It just sucks when that happens, that's all! :D
 
Re: Use Main Breaker or Backfeed on Subpanel?

Originally posted by lcdeyes:
My electrician says he will need to remove the 100A main breaker, and asked me to get a 80A breaker to backfeed the subpanel. He refuses to install the new panel until I do so.
I wonder what his affection is for backfeeding?

As others have stated, the 100 amp breaker is essentially an expensive switch to disconnect all conductors in the detached garage. It could be 200 amps, it doesn't matter.

My electrician says without the 80A incoming breaker on the subpanel, we won't pass, and he will not subject himself to the embarrassment.
Failing inspections isn't fun, but I find it amusing the guy has such deep-rooted revulsion at the thought. :)
 
Re: Use Main Breaker or Backfeed on Subpanel?

Every one of us is always getting educated- some of us a little more than others ;)

Explain to your electrician, that the code section is 408.16(A) - take a look at exception 1.

As has been mentioned, the overcurrent device in the panel at the garage will act as a disconnecting means - which is required in 225.31.

Like Bob has mentioned, changes on a job are the norm today, if there are no changes it comes as a pleasant surprise.
 
Re: Use Main Breaker or Backfeed on Subpanel?

Originally posted by davedottcom:
"About what? A change made in the job. That happens every day"
True. It's just very annoying when people don't know what they want until after the work is completed. This always seems to happen on those jobs that the owner is on the site a lot!
I think Bob's mindset is commendable, but I find myself often falling into yours, Dave.

When time's not an issue, and you call bill for all of it, it's great - you can laugh (to yourself) about all the changes. People. :)

Next thing you know it's scewing up my schedule, and it starts effecting other jobs.
Welcome to my life. :)

I have much to learn when is comes to customer service. As much as I'd like to explain to people at the moment of that everytime they cough it'll cost them $20, I hate to come off as trying to take all their money, or being unfair. But when something takes twice as long as it should have, that time must be accounted for.

I hate it when I end up blindsiding people. I try to avoid it, but I have much to learn. :(
 
Re: Use Main Breaker or Backfeed on Subpanel?

Originally posted by lcdeyes:


He claims that "there is no way" the 80A feeder breaker at the main panel would trip in time to protect the 140 feet of wire from the main to the subpanel, if for some reason the full 100A was attempted to be drawn at the subpanel.
Then again...maybe this guy is just a nut case!
I wonder what he thinks about Main Lug Only Panels?!
;)
 
Re: Use Main Breaker or Backfeed on Subpanel?

Thanks for the "back up" George! ;)

The best way to warn them is to put it something like this:
"Ok, I can give you a really good price but if there are any changes it will be on a time and material basis. That's only fair to both of us."
They always agree and that way there are no surprises when I bill for the extras.
 
Re: Use Main Breaker or Backfeed on Subpanel?

Dave and George if you guys are not getting paid for changes than I guess I could see your point. :D

IMO ripping out work I just put in is not annoying as a matter of fact it is literally money in my pocket. (Assuming the change is not due to my own mistake. ;)

Mainly I just do not see a reason this electrician should be annoyed.

A change to a larger panel, no big deal.

The customer specifies a panel type (very common in big work) EC will not go out his way to provide it (stupid IMO) so the customer had to get it.

JMO, Bob
 