I would like to ask for either electricians opinions or any standard I can site to help justify my use of a (Light blue & Brown conductor) for power input to a control unit we are trying to get UL Listed.
I chose light blue rather than white because it is a widely accepted international standard for power input. The light blue can then be either a grounded or ungrounded conductor.
This control unit accepts "universal" power input in the range for 85 -264V.
In some cases it will be powered by 120V with a grounded neutral and in other cases it may be run from 220, 230, 240 volt supplies (without a grounded conductor).
I feel the Light Blue is the best choice for this application.
The installation diagram clearly shows the input connections when connected to a grounded neutral system to be white->light blue.
Anyone able to cite a justification for or against this decision? I am used to designing to international standards that mandate the use of Light Blue & Brown.
Would you as an electrician feel comfortable with connecting a light blue to a white wire at the field connection point?
I do not like being forced to use a white conductor when in some cases the white would need to be connected to a black or red "hot" conductor.
If use of the Light Blue would be an issue for electricians installing the equipment then I need to reconsider.
I would apppreciate your input.
I chose light blue rather than white because it is a widely accepted international standard for power input. The light blue can then be either a grounded or ungrounded conductor.
This control unit accepts "universal" power input in the range for 85 -264V.
In some cases it will be powered by 120V with a grounded neutral and in other cases it may be run from 220, 230, 240 volt supplies (without a grounded conductor).
I feel the Light Blue is the best choice for this application.
The installation diagram clearly shows the input connections when connected to a grounded neutral system to be white->light blue.
Anyone able to cite a justification for or against this decision? I am used to designing to international standards that mandate the use of Light Blue & Brown.
Would you as an electrician feel comfortable with connecting a light blue to a white wire at the field connection point?
I do not like being forced to use a white conductor when in some cases the white would need to be connected to a black or red "hot" conductor.
If use of the Light Blue would be an issue for electricians installing the equipment then I need to reconsider.
I would apppreciate your input.