Thanks for your input Dan, I see how I was unclear.
Service point (Utility metering) is at 12kv primary switchgear (PSG). PSG has 3 ea fused load interupter switches that feed 3 ea 3000kva 12kv x 480/277V pad mount transformers that feed 3 ea 4000A 480/277V
distribution boards (not services)
I came up with 6 CU AWG EGC for 150A 12kv feeder per 250.122
The 3/0 CU was based on required size of GEC for 3000kva transformers per 250.30(3).
What we would like to accomplish is to efficiently bond each of the grounding electodes present for the building which include 4 separate electrodes for the primary switch gear and each of the 3000kva Transformers. Each of the 3000kva transformers and 4000A distribution boards are located at different areas arround a building where a single grounding grid won't work.
Per 250.50 "All grounding electrodes ... that are present at each building served shall be bonded together to form the grounding electrode system." I didn't see where the code reference necessary size of GEC to accomplish this necessary bonding. This can all be done via feeders from PSG to each of the transformers, but do I need to pull separate EGC and GEC for PSG to each tranformer or would one combined EGC and GEC be sufficient and how to size such combined conductor. Another post with link to a Mike Holt comment disputes the ability to do this.
Appreciate the input