When evaluating ampacity of underground ductbanks for 480V I understand that the code allows for "engineering supervision" (calcs etc..) or provides tables in Annex B as informative information to use/consider for these ampacity calculations. A couple of questions here I was hoping to get some refreshment guidance on:
1) When considering ampacity of underground ductbanks that match one of the arrangements in figure B.2(1) in Annex B do most use the tables in Annex B when access to other engineering evaluation (calculations, software, etc...) is not readily available?
2) For an application where I have (3) single conductor cables in a conduit in underground ductbank Table B.2(7) appears to be the table that would be applicable. When I look at the cable ampacities for a single electrical duct arrangment I notice that the conductor ampacities are actually greater than those listed in Table 310.16. I would expect the tables in Annex B for underground cable to have lesser ampacities given the need to cable to dissipate heat through earth etc...?
3) For Table B.2(7) it appears to have the correction factor table built into the overall table itself as opposed to referencing 310.15(B)(1). I'm assuming that when using these tables you are to use the built in correction factors? Is there a reason why they are listed separately for these underground tables?
4) Although not applicable to my application I notice that Annex B also has tables for cables in free air. I'm curious why these free air tables are listed as part of his Annex if free air values are given in Table 310.17? Are there additional considerations that are included as part of these free air cables in Annex B?
Thanks
1) When considering ampacity of underground ductbanks that match one of the arrangements in figure B.2(1) in Annex B do most use the tables in Annex B when access to other engineering evaluation (calculations, software, etc...) is not readily available?
2) For an application where I have (3) single conductor cables in a conduit in underground ductbank Table B.2(7) appears to be the table that would be applicable. When I look at the cable ampacities for a single electrical duct arrangment I notice that the conductor ampacities are actually greater than those listed in Table 310.16. I would expect the tables in Annex B for underground cable to have lesser ampacities given the need to cable to dissipate heat through earth etc...?
3) For Table B.2(7) it appears to have the correction factor table built into the overall table itself as opposed to referencing 310.15(B)(1). I'm assuming that when using these tables you are to use the built in correction factors? Is there a reason why they are listed separately for these underground tables?
4) Although not applicable to my application I notice that Annex B also has tables for cables in free air. I'm curious why these free air tables are listed as part of his Annex if free air values are given in Table 310.17? Are there additional considerations that are included as part of these free air cables in Annex B?
Thanks