Use of Article 220.5(B) on single loads
DST Engineer
New User
Long Island, NY
I have a Make Up Air Unit that requires two feeds. (1) for the heating element for the space and (1) for the exhaust fan. The heating element is 48.1amps. This is a continuous load per Article 224 which gets us 60.125 amps (48.1*1.25).
Can I use Article 220.5(B) to reduce the continuous load to 60 amps (round to the nearest whole amp) to size my breaker and conductors? Or do I have to size conductors and circuit breakers to ampacity of the unit and the continuous load (60.125A). I just used the example above as context, but curious what the community thinks.
P.S. big thanks to Dennis Alwon, charlie b, and everyone in this forum. You've helped me so much in my career.