Use of Frame as EGC NEC17

Status
Not open for further replies.

00crashtest

Senior Member
Location
California
Occupation
electrician trainee
In the 2017 edition of the National Electric Code, on page 125, 250.136(A), titled Equipment Secured to Grounded Metal Supports, says, "The structural metal frame of a building shall not be used as the required equipment grounding conductor for ac equipment." Since it makes no mention of dc, does this mean that DC equipment is always allowed, unless there are other restrictions, to use buulding frames as the required EGC? In general, if the authority having jurisdiction hasn't made additional relevant restrictions, does the NEC work like common law, where such thing is not explicitly prohibited (in any direct or indirect way) is always allowed? Or does it instead work like civil law where such thing is not explicitly allowed is always prohibited?
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
DC equipment requiring an EGC would still need an EGC listed in 250.118. So your question is pretty moot in this case. But in general, things not prohibited by the NEC are allowed. (I don't think your characterization if civil law is correct, btw.)
 