At our plant, our crane repair personnel require the electrical department to put up grounding straps by shorting our dc crane rails and connecting to ground. Our system is 250 vdc ungrounded. Crane repair is led to believe that these grounding straps will protect them if the power is put back while they are working by the hotrails. We use proper lock out tag out procedures. We recently had a instance where the power was put in and the ground straps were not removed. The straps burned for at least 5 minutes and blew open. Our thermal magnetic breaker never tripped. In my 35 years experience, I have seen this happen at least ten times. We have been trying to convince our company to get rid of this practice of grounding straps. These strps are the the largest straps we can buy from Sailisbury (4/0) and they are not rated for DC. Now they are talking about running 1000 kcmil cable to a disconnect with a Kirk-key application and making that disconnect into a deliberate short circuit if the power goes in. They base their criteria on principles of grounding straps used by high voltage workers on AC circuits. I am saying that we are creating more danger by using th grounding straps that what we are trying to prevent. We are saying that lock out and tag out is that best and only measure that should be used. I would like to here some expert opinion on this subject. Am I off base here by disagreeing with these grounding straps and a so called short cicuit disconnect they are thinking about installing?