Use of HCF cable to feed recepticles in a Healthcare Fac

Status
Not open for further replies.

vinchenzo

Member
One of my co-workers told me that HCF cable can't be used to feed recepticles connected to emergency power. Is this true?
 
Re: Use of HCF cable to feed recepticles in a Healthcare Fac

Jim,

HCF is Type AC cable, since the jacket is a listed grounding path. MC cable jacket is not suitable for grounding.
 
Re: Use of HCF cable to feed recepticles in a Healthcare Fac

Vinchenzo, he/she is correct in the 2002 nec cycle, see 517.30(C)(3)

There are added exceptions in the 2005, that will add some allowances.

Roger

[ January 03, 2005, 09:16 PM: Message edited by: roger ]
 
Re: Use of HCF cable to feed recepticles in a Healthcare Fac

Roger,

After reading 517.30(C)(3)I came to the same conclusion but was hoping that I was missing something. Oh well - live and learn! Thanks everyone.
 