jrtinwa
Member
- Location
- Gig Harbor, WA
Just looking to have a general discussion on the use of shore power adapters in marinas. I am reviewing the electrical integrity of our marina shore power system and I am finding some interesting things. Our marina was wired before the NFPA and NEC main GFEP protection requirement so does not have it on the main OCD or on any of the shore power connections.
Case#1 Good or Not Good?
Case#2 Good or Not Good?
Case#3 Good or Not Good?
Case#4 Good or Not Good?
Case#1 Good or Not Good?
Breaker 30A SP
Outlet 50A 125V (SS-1)
Cord 50A 125V to 30A 125V adapter to marine 10/3 shore power cord
NEC 555.19.A.3 and 210.21.B seem to say that the breaker and outlet must match
Outlet 50A 125V (SS-1)
Cord 50A 125V to 30A 125V adapter to marine 10/3 shore power cord
NEC 555.19.A.3 and 210.21.B seem to say that the breaker and outlet must match
Case#2 Good or Not Good?
Breaker 50A SP
Outlet 50A 125V (SS-1)
Cord 50A 125V to 30A 125V adapter to marine 10/3 shore power cord
The breaker and outlet match but are adapted directly to a 30 amp system protected by a 50A breaker
Outlet 50A 125V (SS-1)
Cord 50A 125V to 30A 125V adapter to marine 10/3 shore power cord
The breaker and outlet match but are adapted directly to a 30 amp system protected by a 50A breaker
Case#3 Good or Not Good?
Breaker 50A SP
Outlet 50A 125V (SS-1)
Cord 50A 125V to double 30A 125V adapter to one marine 10/3 shore power cord
The breaker and outlet match but are adapted directly to a double 30 amp system protected by a 50A breaker with only one 30A connection used
Outlet 50A 125V (SS-1)
Cord 50A 125V to double 30A 125V adapter to one marine 10/3 shore power cord
The breaker and outlet match but are adapted directly to a double 30 amp system protected by a 50A breaker with only one 30A connection used
Case#4 Good or Not Good?
Breaker 30A SP
Outlet30A 125V (L5-30)
Cord 30A 125V to 15A straight adapter to straight 12/3 shore power cord
The breaker and outlet match but are adapted directly to a 15A system
protected by a 30A breaker and the 15A connection if not GFCI protected
or locking style. Looks like an obvious "Not Good"
Outlet30A 125V (L5-30)
Cord 30A 125V to 15A straight adapter to straight 12/3 shore power cord
The breaker and outlet match but are adapted directly to a 15A system
protected by a 30A breaker and the 15A connection if not GFCI protected
or locking style. Looks like an obvious "Not Good"