As long as it's in Miami I think it's ok.On a recent high rise buiding inspection in Miami I ran into this mess. Does anyone see any problems? All NM Flex was recently installed and there was no electrical permit pulled.
On a recent high rise buiding inspection in Miami I ran into this mess. Does anyone see any problems? All NM Flex was recently installed and there was no electrical permit pulled.
not permitted where: ambient temps exceed 122 degrees f. i bet it gets hotter than that up on that roof deck ? 362.12 (3) 2011 nec. and, where exposed to direct rays of the sun, unless identified as sunlight resistant 362.12 (8), 2011 nec
On a recent high rise buiding inspection in Miami I ran into this mess. Does anyone see any problems? All NM Flex was recently installed and there was no electrical permit pulled.
The galvanized 'straps' are improper supports, not designed for the purpose and vibration eventually cause it to cut into the NM and conductors.
The unistruts supporting the NM ar mouted directly of of the AHU's frame. No vibration there......right.:huh:I have used metal straps for carflex for almost 30 years -- there should not be much vibration that far away. However with the sun heating the carflex it may make it more susceptible to the strap digging in.