I have been asked to investigate the viability and possible cost savings of recommendations arising from a ?Value Engineering? review. The project includes several large buildings. One recommendation is to replace the current design of ?conduit and wire? with a design that uses MC cable, for feeders up to 1200 amps.
Example: Our current design has four parallel sets of 350 MCM cable, each including a 3/0 EGC, for the feeder to a 1200 panel. OK, so I can replace that with four parallel 350 MCM MC cables. But each cable would have to have a ?full size? ground, per 250.122F. My problem is figuring out how to get an MC cable with 350 MCM conductors and a 3/0 ground wire. Does anyone make such an animal? One manufacturer?s catalog that I have on my desk says that the EGC in a 350 MCM MC cable is size 3.
As I see it now, I can?t feed a panel rated higher than 225 amps with a single MC cable. Beyond that, I need parallel MC cables, and I can?t get an EGC large enough in an MC to allow parallel cables.
Any ideas or experiences to offer?
Example: Our current design has four parallel sets of 350 MCM cable, each including a 3/0 EGC, for the feeder to a 1200 panel. OK, so I can replace that with four parallel 350 MCM MC cables. But each cable would have to have a ?full size? ground, per 250.122F. My problem is figuring out how to get an MC cable with 350 MCM conductors and a 3/0 ground wire. Does anyone make such an animal? One manufacturer?s catalog that I have on my desk says that the EGC in a 350 MCM MC cable is size 3.
As I see it now, I can?t feed a panel rated higher than 225 amps with a single MC cable. Beyond that, I need parallel MC cables, and I can?t get an EGC large enough in an MC to allow parallel cables.
Any ideas or experiences to offer?