San Jose has started enforcing a code interpretation that states for offices and banks we cannot use Table 220.44 diversity factors for receptacle loads when sizing feeders, panels or equipment, even if we use 220.14 (H or I) as the larger number to 220.14(K)1 or 2 for offices or bank receptacle branch loads.
The City Inspection stated that they just had a training a few weeks ago and this was brought up during their training session.
We tried to go to NFPA and pose the technical question to see if this is correct, hoping we can get the interpretation as we know it, but a NFPA technical specialist also stated that we cannot use 220.44 diversity of receptacles for offices and banks.
Not sure if NFPA is providing this training.
Both NFPA specialist and City of San Jose are stating that we must calculate office or bank loads at 100% to calculate feeder and equipment sizes.
We are wondering if anyone else in the industry has encountered this issue.
The City Inspection stated that they just had a training a few weeks ago and this was brought up during their training session.
We tried to go to NFPA and pose the technical question to see if this is correct, hoping we can get the interpretation as we know it, but a NFPA technical specialist also stated that we cannot use 220.44 diversity of receptacles for offices and banks.
Not sure if NFPA is providing this training.
Both NFPA specialist and City of San Jose are stating that we must calculate office or bank loads at 100% to calculate feeder and equipment sizes.
We are wondering if anyone else in the industry has encountered this issue.