Hi Everyone,
I would like to get your thoughts on a few questions surrounding the use of TC-ER cable as permitted by NEC 336.10.
I would like to get your thoughts on a few questions surrounding the use of TC-ER cable as permitted by NEC 336.10.
- If a TC-ER exits a tray to connect to a device/equipment, 336.10 (7) c) mentions that it should be continuously supported. 336.10 (7) e) also goes on to say that the cable must be secured every 6 ft or less. I have seen installations where TC-ER cable exits a tray and goes several feet to equipment without a strut/channel as it's not practical. Is this correct? Are they using the Exception to (7) rule which allows TC-ER cables to extend without continuous support upto 6ft?
- What is the point of having an -ER (-Exposed Run) classification per UL 1277 where the cable has to meet impact and crush tests similar to MC cables if it can only run a max of 6ft without continuous support?
- Further to the 'Exception to (7)' rule, what if a TC-ER cable (in industrial / commercial applications) exits a tray and is longer than 6ft without continuous support? Is this simply not allowed? What if it is supported/secured by brackets / clips every few feet and installed on a wall but not in a channel / strut?
- Is there any way a TC-ER cable can be installed without any tray anywhere and is simply installed on a wall using special brackets? I ask because I am seeing new proprietary flat cables that are TC-ER rated and meant for installation on a wall directly.