All of the circuit conductors would be in the same trench, but would not be in the same cable. It is my opinion that the separate EGC is a violation of this code section.300.3(B) Conductors of the Same Circuit. All conductors of the same circuit and, where used, the grounded conductor and all equipment grounding conductors and bonding conductors shall be contained within the same raceway, auxiliary gutter, cable tray, cablebus assembly, trench, cable, or cord, unless otherwise permitted in accordance with 300.3(B)(1) through (B)(4).
You can read the code section that applies to say that you can't use a separate EGC with the USE cable, or that you can.
All of the circuit conductors would be in the same trench, but would not be in the same cable. It is my opinion that the separate EGC is a violation of this code section.
run this type of install all the time. trench is not a raceway in my opinion. we use 4/0 use and a #4 use ground all the time for trailers and mfg homes. also have used 2/2/4 use w a separate ground for garages and outbuildings when we can't find 2/2/2/4.
It does include "trench" and "or" in the list. I say compliant.You can read the code section that applies to say that you can't use a separate EGC with the USE cable, or that you can.
All of the circuit conductors would be in the same trench, but would not be in the same cable. It is my opinion that the separate EGC is a violation of this code section.
It does include "trench" and "or" in the list. I say compliant.
code compliant in my opinion no question.
So based on that I could install GRC for some of the conductors and lay the others beside it?
That is what I was trying to figure out. I guess in a trench you could? But I wouldnt think so.
code compliant in my opinion no question.
I think he is asking about buying a 3-wire USE assembly, and adding a single grounding conductor in the same trench with it......NOT a seperate trench.
If so, I do that all the time.