I was recently called to give an estimate on installing a used 1996 Cal Spa hot tub. It will be installed on a concrete patio, next to the home. I haven't installed a hot tub in a while so I want to double check. The NEC 2014 680.26 (B) says the following:
Equipotential bonding of perimeter surfaces in accordance with 680.26(B)(2) shall not be required to be provided for spas and hot tubs where all of the following conditions apply:
?The spa or hot tub shall be listed as a self-contained spa for aboveground use.
?The spa or hot tub shall not be identified as suitable only for indoor use.
?The installation shall be in accordance with the manufacturer?s instructions and shall be located on or above grade.
?The top rim of the spa or hot tub shall be at least 710 mm (28 in.) above all perimeter surfaces that are within 760 mm (30 in.), measured horizontally from the spa or hot tub. The height of nonconductive external steps for entry to or exit from the self-contained spa shall not be used to reduce or increase this rim height measurement.
So I'm I right in thinking that since this is a self-contained spa, equipotential bonding is not required?
Also, I'm a little afraid of installing a unit built in 1996. Fear there is a ton of things that could go wrong with that that I will be blamed for. How many of you would take on this task?
Thanks ahead of time for your responses and help. I appreciate it.
Equipotential bonding of perimeter surfaces in accordance with 680.26(B)(2) shall not be required to be provided for spas and hot tubs where all of the following conditions apply:
?The spa or hot tub shall be listed as a self-contained spa for aboveground use.
?The spa or hot tub shall not be identified as suitable only for indoor use.
?The installation shall be in accordance with the manufacturer?s instructions and shall be located on or above grade.
?The top rim of the spa or hot tub shall be at least 710 mm (28 in.) above all perimeter surfaces that are within 760 mm (30 in.), measured horizontally from the spa or hot tub. The height of nonconductive external steps for entry to or exit from the self-contained spa shall not be used to reduce or increase this rim height measurement.
So I'm I right in thinking that since this is a self-contained spa, equipotential bonding is not required?
Also, I'm a little afraid of installing a unit built in 1996. Fear there is a ton of things that could go wrong with that that I will be blamed for. How many of you would take on this task?
Thanks ahead of time for your responses and help. I appreciate it.