used genny and transfer switch

Status
Not open for further replies.

GerryB

Senior Member
A friend of mine is concerned (overly I think) over control wires for a generator. He has a new house with power lines out to the genny location, but no control wires were run. He bought a used 16 k generac and a Briggs and Stratton ATS. The manuel says to run 16-5 control wire. I told him as did another electrician that 18-5 is fine. (with 300 volt insulation). He's very handy and wants to do it himself. To confuse him further a Generac tech told him he can't use 18 gauge because it's 240 volt, and that he runs a 14-3 and a 14-2 romex, (makes no sense to me). Any one think there is any issue with 18 gauge wire with 300 volt insulation?
 
Back up a bit.... I’m not sure the Generac genny will work with a Briggs and Stratton transfer switch anyway.
 
In those Generac transfer switches the 240V goes out to the generator thru two 10A (I think) fuses. Generac uses a dumb transfer switch in that the the loss of that 240V at the generator is what starts it. If the B&S is a smart switch (meaning it tells the generator to start) then you may be able to use a simple two wire to start it, depending on what controller is in the generator.


Sent from my iPhone using Tapatalk
 
In those Generac transfer switches the 240V goes out to the generator thru two 10A (I think) fuses. Generac uses a dumb transfer switch in that the the loss of that 240V at the generator is what starts it. If the B&S is a smart switch (meaning it tells the generator to start) then you may be able to use a simple two wire to start it, depending on what controller is in the generator.


Sent from my iPhone using Tapatalk
Thanks, I am going to see it today. It looked like you needed 4 wires on the diagram, two going to the N1 n2 .
 