User Generated Control Drawings for Intrinic Safety

Status
Not open for further replies.
Is it acceptable to connect a non-rated 24 VDC powered, 4-20 ma signal output load cell to an appropriate barrier, to meet Class I, Div 2 Group B Intrinic Safety requirements provided that the entity paramaters, wiring, etc. is documented on a user generated control drawing? The load cell itself does not have a control drawing or IS certification and is not capable of being located in a purged enclosure. If generating a user control drawing is not an acceptable practice are any other options avaialbe for this hazard area.
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Is it acceptable to connect a non-rated 24 VDC powered, 4-20 ma signal output load cell to an appropriate barrier, to meet Class I, Div 2 Group B Intrinic Safety requirements provided that the entity paramaters, wiring, etc. is documented on a user generated control drawing? The load cell itself does not have a control drawing or IS certification and is not capable of being located in a purged enclosure. If generating a user control drawing is not an acceptable practice are any other options avaialbe for this hazard area.
A control drawing, whether for intrinsically safe (IS) or nonincendive (NI) systems, is by definition generated by the appropriate apparatus' manufacturer. [See the definition in Section 500.2] A manufacture's control drawing for the barrier itself may be sufficient. BTW, you only need NI in Division 2.
 
Status
Not open for further replies.