Twoskinsoneman
Senior Member
- Location
- West Virginia, USA NEC: 2020
- Occupation
- Facility Senior Electrician
If the type of wire is not found in Table 310.16 how can you find the ampacity? Can you just match up the operating temp?
If the type of wire is not found in Table 310.16 how can you find the ampacity? Can you just match up the operating temp?
NFPA 79 states that 310.16 and 310.17 should be used for ampacity of MTW. I would assume you would just use the corresponding temperature rating of the MTW.
Lots of times MTW is part of a dual listing THWN/MYW...
Not is the sense that you are using the word "true".All of the #12 my supply house stocks is marked like this: E51583 S (UL) AWG 12 CU TYPE MTW OR THWN OR THHN OR GASOLINE AND OIL RESISTANT II OR AWM 600 VOLTS VW-1 ---c (UL) T90 NYLON ORTWN75 FT1. Is it "true" MTW ?
benaround, using the 16 AWG to wire in a second Emergency Stop switch on an existing CNC milling machine.
Thank you topgone, this is to stop a 24VDC control circuit drawing 6.3A max so the 16AWG will do. I figured it was more than enough but working in an industrial setting its good to have the facts. I am not familiar with the NFPA 79, is this a cut directly from a page in the NFPA 79 reference book? Also, do you know if this information exists in the NEC 2008 NFPA 70 reference book?
Leo