Hello,
I am working on a control system which contains devices in a classified area (class 1, div1 --Alcohol vapors normally present). I have selected all intrinsically safe devices and am using an intrinsically safe barrier. My layout is like this:
|.........control enclosure..........|
|unclassified area (outside) |-------->|SEAL OFF|------->| classified area with field devices|
|IS barrier for all IO.................|
I would like a check on my understanding:
Additional information:
Thank you for your time and assistance!
I am working on a control system which contains devices in a classified area (class 1, div1 --Alcohol vapors normally present). I have selected all intrinsically safe devices and am using an intrinsically safe barrier. My layout is like this:
|.........control enclosure..........|
|unclassified area (outside) |-------->|SEAL OFF|------->| classified area with field devices|
|IS barrier for all IO.................|
I would like a check on my understanding:
- The seal off is placed to prevent vapor from returning to the control enclosure
- Once in the classified area, do I need class 1 div1 rated conduit and misc. parts if the devices and source are intrinsically safe?
- I'm not sure why I would, if the current is limited from the barrier, there shouldn't be any risk within the conduit. But I could be wrong on this.
- Can someone please point me to the relevant code sections?
Additional information:
- Field devices are 24vdc and 12vdc
- There are a few pneumatic valves with IS components and asco IS rated solenoids
- Aside from that, it's flow meters and switches all IS
Thank you for your time and assistance!