IS it possibly to connect a transformer after the output of a UPS?. doing this have any trouble?
On some models of UPS there is a "walk in" to avoid the possible problems with transformer inrush or other loads with high initial currents like incandescent lamps.Fortunato Garmendia said:IS it possibly to connect a transformer after the output of a UPS?. doing this have any trouble?
I agree and welcome to the forum.Besoeker said:Check the specification is probably the best advice.
Assuming that the UPS is equiped with a bypass of course.brian john said:Transformers are connected downstream from UPS systems all the time ie 480/277 VAC output to 480-208/120 VAC PDU's. UPS's can handle a certain percentage of overload for in rushes, if the in rush exceeds this value the UPS will go to bypass, after a predetermined period of time the UPS will return to normal operation