I have a job where customer has a 450 sq ft 1 bedroom apt sharing a 8 meter meter center that is fused at 250 amps ( 240/120 1 phase ).
Present service is 60 amps ( gas range ), electric water heater.
He wants to install a mini-split with a horizontal canister in the hallway ( drop the hallway ceiling ) using a 12000 btu heat pump. ( draws less than 10 amps @240 v )
It is in Miami, so I am not to concerned about supplemental heat since unit will work down to 5 degrees F.
My question is ....when I do a load calc for the unit, do I need to add the "fake" 8000 va load for the apt making it tight for the load calc of the unit, or only for all 8 units
in the total load calc which is allowing me to use the 200.84 43% demand factor ?
The complex has a separate existing 100 amp service feeding the added laundry room with 2 washers and 2 dryers and small outside ltg circuit polaris tapped to the overhead service..
Thanx, DHSVCS
Present service is 60 amps ( gas range ), electric water heater.
He wants to install a mini-split with a horizontal canister in the hallway ( drop the hallway ceiling ) using a 12000 btu heat pump. ( draws less than 10 amps @240 v )
It is in Miami, so I am not to concerned about supplemental heat since unit will work down to 5 degrees F.
My question is ....when I do a load calc for the unit, do I need to add the "fake" 8000 va load for the apt making it tight for the load calc of the unit, or only for all 8 units
in the total load calc which is allowing me to use the 200.84 43% demand factor ?
The complex has a separate existing 100 amp service feeding the added laundry room with 2 washers and 2 dryers and small outside ltg circuit polaris tapped to the overhead service..
Thanx, DHSVCS