Using 310.15(B)(16) for Less Than 100A

Status
Not open for further replies.
All,

I know somewhere in the code, it states for circuits 100A or less, you are to use the 60-degree C column for selecting conductor size but can't seem to locate it.

Any help finding will be greatly appreciated.

Thanks,

Steve
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
110.14(C)
but note the 75° column can be used if all terminations are rated 75°
 

qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
All,

I know somewhere in the code, it states for circuits 100A or less, you are to use the 60-degree C column for selecting conductor size but can't seem to locate it.

Any help finding will be greatly appreciated.

Thanks,

Steve

Maybe.....

110.14 (C) (1) (a) (1) & (2)
2104 NEC
 