i think this video with the example at the 16 minute mark may be incorrect. 300amp continuous load from breaker to junction box 300x1.25= 375amp wire 500kcm wire at 75 degrees 380amp agreed. Splice box to splice box load at 100% of continuous so 300amp wire required not 380 so my opinion is at 90C 300kcm is adequate. The video shows 400kcm at 380amps required. please help with what im missing