No equipment below 600 V exists listed for 90c operation. It has never bean allowed or permitted, due to listing violations.
CAUTION ON USING LUG RATINGS
Manufacturers commonly use 90 °C-rated lugs (i.e., marked AL9CU) on equipment rated only 60 °C or 75 °C. The use of the 90 °C-rated lug in this type of equipment does not allow the installer to use 90 °C wire at the 90 °C ampacity. The Underwriters Laboratories® General Information on Electrical Equipment Directory states the following about terminations: “A 75 °C or 90 °C temperature marking on a terminal (e.g., AL7, CU7AL, AL7CU or AL9, CU9AL, AL9CU) does not in itself indicate that a 75 °C or 90 °C insulated wire can be used unless the equipment in which the terminals are installed is marked for 75 °C or 90 °C.”
For electrical equipment rated for 600 V and less, terminations are typically rated at 60 °C, 75 °C or 60/75 °C. No distribution or utilization equipment is listed and identified for the use of 90 °C wire at its 90 °C ampacity. This includes distribution equipment, wiring devices, transformers, motor control devices, and even utilization equipment such as HVAC, motors, and light fixtures. Installers and designers who have not realized this fact have equipment that does not comply with the National Electrical Code and that has been turned down by the electrical inspector.
Some equipment requires the conductors that are terminated in the equipment to have an insulation rating of 90 °C, but an ampacity based on 75 °C or 60 °C. This type of equipment might include 100% rated circuit breakers, fluorescent lighting fixtures, etc., and is marked to indicate such a requirement.