Twoskinsoneman
Senior Member
- Location
- West Virginia, USA NEC: 2020
- Occupation
- Facility Senior Electrician
Another gem from the MH NEC DVDs I'd like to get opinions on. One of the guys on MH's little panel said the following would be compliant.
Run a circuit using 90 degree wire to a 90 splice (and use it as the ampacity listed in the 90 degree column) and then from the splice run wire with ampacity from 75 degree column to 75 degree rated equip. (or 60 degree depanding on situation)
Does anyone consider it a violation if the wire using in the 90 degree portion of circuit would be undersized if used as the 75 or 60?
If this is so I think we could be saving a lot of money on longer runs of larger size wire