turtlepokerman
Member
- Location
- USA
- Occupation
- Electrical
Greetings,
I'm going a little crazy here with the "equipment ground" versus a "bonding ground". What I currently have is a feeder cable that goes from a 70A - 480V feeder breaker to a 100A Disconnect switch. The cable is a 3/C #4 w/ gnd cable routed through aluminum emt conduit. The inspector on site says that I need bonding bushings on both ends of the conduit to maintain electrical continuity between the panels and the disconnect switch. The current conduit fittings are not UL listed as a grounding means.
Why would I need the conduit bushing on both ends of the raceway if I run a ground conductor in the cable? If a fault occurs in the raceway, the fault current would go through the equipment ground in the cable. Am I missing something?
Any help is appreciated.
I'm going a little crazy here with the "equipment ground" versus a "bonding ground". What I currently have is a feeder cable that goes from a 70A - 480V feeder breaker to a 100A Disconnect switch. The cable is a 3/C #4 w/ gnd cable routed through aluminum emt conduit. The inspector on site says that I need bonding bushings on both ends of the conduit to maintain electrical continuity between the panels and the disconnect switch. The current conduit fittings are not UL listed as a grounding means.
Why would I need the conduit bushing on both ends of the raceway if I run a ground conductor in the cable? If a fault occurs in the raceway, the fault current would go through the equipment ground in the cable. Am I missing something?
Any help is appreciated.