I have a 240 volt 3 phase system/service with a high leg. They are using 3 pole circuit breakers (in the Main Distribution Panel) to feed various single phase panelboards. Leaving one phase of the circuit breaker open (high leg). Is this acceptable?
The panel is only marked with a sharpie. Hand written on the cover. The 'C' phase conductor has tape on it stating 'High Leg'.I'm going to go out on a limb here and say, no. It would not be prudent.
Is the panel board clearly marked, labeled?
Is it field constructed thing or a listed assembly that happens to look like four poles (even if it sort of is)?Hi, I have a 415V 3Ph 4 wire Distribution Board in which one feeder is connected to a single phase industrial socket outlet. This feeder has 4 Pole circuit breaker converted into a 2 Pole circuit breaker 250V through wiring. Please show standard stating this procedure.
The IEC or BS doesn't care either. No problem with a single phase load thru 1 pole of a three phase breaker.... as stated by others, it'll still work the same.Is it field constructed thing or a listed assembly that happens to look like four poles (even if it sort of is)?
Please also note that 415 volts isn't really a NEC or NEMA standard voltage so the IEC standards that likely apply might not be quite the same as NEC and NEMA standards either.
The IEC or BS doesn't care either. No problem with a single phase load thru 1 pole of a three phase breaker.... as stated by others, it'll still work the same.
I understand that, but isn't the question about paralleling overcurrent devices to effectively make a higher setting device?The IEC or BS doesn't care either. No problem with a single phase load thru 1 pole of a three phase breaker.... as stated by others, it'll still work the same.
In fact, IIRC for some breaker lines, they do not make straight rated 2 poles, so the manufacturer will tell you to use a three-pole.All breakers tested to UL 489 have been tested using all pole combinations.
The practice in the OP is actually quite common.
Or in some cases I have seen two pole breakers in a three pole frame.In fact, IIRC for some breaker lines, they do not make straight rated 2 poles, so the manufacturer will tell you to use a three-pole.
In a few cases I have seen three pole breakers with two poles with two poles looped on to the third pole of the breaker.Or in some cases I have seen two pole breakers in a three pole frame.
Mostly only see that sort of thing here in the US with motor overload relays that offer phase loss protection of some sort but they are only supplying a single phase motor. All three poles will need to see a certain amount of current balance or it will trip those devices.In a few cases I have seen three pole breakers with two poles with two poles looped on to the third pole of the breaker.