using a #6 copper ground with aluminum feeders

Status
Not open for further replies.

rydan

Member
Location
RPB, Fl.
I have a neighbor running 3/0 aluminum wire to feed a 150 amp panel for his shed. Will the inspector have an issue with using a #6 copper ground wire. ?
 
I have a neighbor running 3/0 aluminum wire to feed a 150 amp panel for his shed. Will the inspector have an issue with using a #6 copper ground wire. ?

take a look at table 250.122. note that the minimum size of the EGC is determined solely by the rating of the upstream OCPD and can be either AL or CU as noted in the table.
 
I have a neighbor running 3/0 aluminum wire to feed a 150 amp panel for his shed. Will the inspector have an issue with using a #6 copper ground wire. ?
If you are asking whether there is a problem with pairing a copper grounding conductor with aluminum circuit conductors, the answer is no.
 