Our European office uses a 0.5HP drum motor, from a small, specialized manufacturer, on a conveyor application which has a nominal nameplate voltage 181V and with a 230V 1HP VFD.
My office wants to replace a 1HP induction motor that is side mounted on a different kind of conveyor application with the previously mentioned drum motor. Mainly because of the special environmental and IP rating offered by this motor. This conveyor application uses 1HP VFDs but they are 480V supply rated.
They ordered some of these motors to do this replacement test on some conveyor equipment, that is already built here. Just to see if it preforms well enough or if they need to put back in the side mounted induction motors, before it gets shipped out.
The problem, I think, is that they think the current 1HP VFD is sufficiently power rated to use a 0.5HP motor and thus we don't need to swap out VFDs. We just need to change the VFD parameters to correspond to the new drum motor.
Well...the minimum nominal output voltage I can set for these 480V 1HP VFDs is 200V, which is higher than that 181V I mentioned in the first sentence.
Not really sure how big of a deal a 10% higher voltage supplied to the motor will be but I wouldn't be surprised. Not really concerned about speed or torque performance, we don't necessarily need anything accurate, but worried about just frying the motor.
And we don't have any 230V 1HP VFDs on hand either.
My office wants to replace a 1HP induction motor that is side mounted on a different kind of conveyor application with the previously mentioned drum motor. Mainly because of the special environmental and IP rating offered by this motor. This conveyor application uses 1HP VFDs but they are 480V supply rated.
They ordered some of these motors to do this replacement test on some conveyor equipment, that is already built here. Just to see if it preforms well enough or if they need to put back in the side mounted induction motors, before it gets shipped out.
The problem, I think, is that they think the current 1HP VFD is sufficiently power rated to use a 0.5HP motor and thus we don't need to swap out VFDs. We just need to change the VFD parameters to correspond to the new drum motor.
Well...the minimum nominal output voltage I can set for these 480V 1HP VFDs is 200V, which is higher than that 181V I mentioned in the first sentence.
Not really sure how big of a deal a 10% higher voltage supplied to the motor will be but I wouldn't be surprised. Not really concerned about speed or torque performance, we don't necessarily need anything accurate, but worried about just frying the motor.
And we don't have any 230V 1HP VFDs on hand either.