Mr. Serious
Senior Member
- Location
- Oklahoma, USA
- Occupation
- Electrical Contractor
I have a used panelboard that I removed from a job site a few months ago, a Siemens 250A 42-circuit panel with a 100A main breaker installed.
I know there's a general prohibition against re-using electrical equipment, but this is in very good condition and I think the inspector will allow it. I hesitate because the marked voltage is different. The panelboard is labeled for 208Y120 and I would be using it on 240Δ120 high-leg service. Is that likely to present any additional problem, or do you think if the inspector agrees to allow a used panelboard, they'll also be OK with the different voltage?
The jurisdiction is City of Tulsa. The panelboard is labeled P1C42BL100CTS. Page 4 of this document shows how Siemens part numbers work. This was originally a 100A main breaker panel for 208Y120, but I see no problem with adding lugs and feeding it from 200A fuses on a 240Δ120, and probably using the 100A breaker for a sub-feed. I recognize that any 2-pole breakers using the high leg will have to be upgraded to 240V-rated instead of 120/240V.
I know there's a general prohibition against re-using electrical equipment, but this is in very good condition and I think the inspector will allow it. I hesitate because the marked voltage is different. The panelboard is labeled for 208Y120 and I would be using it on 240Δ120 high-leg service. Is that likely to present any additional problem, or do you think if the inspector agrees to allow a used panelboard, they'll also be OK with the different voltage?
The jurisdiction is City of Tulsa. The panelboard is labeled P1C42BL100CTS. Page 4 of this document shows how Siemens part numbers work. This was originally a 100A main breaker panel for 208Y120, but I see no problem with adding lugs and feeding it from 200A fuses on a 240Δ120, and probably using the 100A breaker for a sub-feed. I recognize that any 2-pole breakers using the high leg will have to be upgraded to 240V-rated instead of 120/240V.