I perform engineering design work in petrochemical plants with lots of pole lines. These pole lines have phase cables wrapped around a steel messenger. The voltage of these circuits range from 120V through 13,800V.
My question is can the steel messenger be used as an EGC? The NEC doesn't list messenger as one of the 14 acceptable EGCs, but would the NESC apply in this case? In residential installations, I have noticed utilities using the messengers for EGCs back to the pole transformers. The NESC doesn't say much about EGCs and it doesn't appear that the NESC even requires EGCs. Open wire utility lines don't have EGCs. The small static wire above a utility line is for lightning protection and is not close to having the ampacity required for an EGC. What are the NESC requirements for EGCs?
Thanks in advance for your comments.
My question is can the steel messenger be used as an EGC? The NEC doesn't list messenger as one of the 14 acceptable EGCs, but would the NESC apply in this case? In residential installations, I have noticed utilities using the messengers for EGCs back to the pole transformers. The NESC doesn't say much about EGCs and it doesn't appear that the NESC even requires EGCs. Open wire utility lines don't have EGCs. The small static wire above a utility line is for lightning protection and is not close to having the ampacity required for an EGC. What are the NESC requirements for EGCs?
Thanks in advance for your comments.