I AM WIRING A 3 PHASE 480 VOLT 50 HP MOTOR NAMEPLATE AMPS 65. I WANT TO USE A VFD FOR A PHASE CONVERTOR. I HAVE ON SITE 240 VOLT SINGLE PHASE. IM PLANNING TO INSTALL A 240 VOLT TO 480 VOLT SINGLE PHASE TRANSFORMER TO FEED LINE SIDE OF VFD AT 480 VOLT SINGLE PHASE
. MY QUESTIONS ARE #1-HOW DO I PROPERLY SIZE VFD? DO I GO UP 2 SIZES AS A RULE OF THUMB . #2-DO I SIZE SINGLE PHASE TRANSFORMER TO THE SIZE OF THE 50 HP MOTOR (65 AMPS X 1.73 =112.45 AMPS ) 240 X 112.45/1000 =27.12 KVA TRANSFORMER OR TO THE HP RATING OF THE VFD.(I THINK I SIZE TO THE VFD RATED HP)THATS 2 SIZES BIGGER .#3-IF I FUSE TRANSFORMER AT 125% ON PRIMARY SIDE WOULD I HAVE TO INSTALL OCP BETWEEN LOAD SIDE OF VFD (480 3 PHASE) AND MOTOR AT 175%. THANKS HOPEFULLY NOT TO CONFUSING
. MY QUESTIONS ARE #1-HOW DO I PROPERLY SIZE VFD? DO I GO UP 2 SIZES AS A RULE OF THUMB . #2-DO I SIZE SINGLE PHASE TRANSFORMER TO THE SIZE OF THE 50 HP MOTOR (65 AMPS X 1.73 =112.45 AMPS ) 240 X 112.45/1000 =27.12 KVA TRANSFORMER OR TO THE HP RATING OF THE VFD.(I THINK I SIZE TO THE VFD RATED HP)THATS 2 SIZES BIGGER .#3-IF I FUSE TRANSFORMER AT 125% ON PRIMARY SIDE WOULD I HAVE TO INSTALL OCP BETWEEN LOAD SIDE OF VFD (480 3 PHASE) AND MOTOR AT 175%. THANKS HOPEFULLY NOT TO CONFUSING