Using a white #12 wire marked as a hot for 220 applications

Jhon123

Member
Location
LA
Occupation
Electrician
Im being told I cannot phase a white wire (12/2 romex) going to ac disconnect with no neutral required but i understand that as long as is cable,permanently marked with like phase marker we should be good ? 200.7
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Yes you can re-identify a white conductor within a cable as an ungrounded conductor. This is done everyday with 240 volt circuits.

Welcome to the Forum. :)
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Im being told I cannot phase a white wire (12/2 romex) going to ac disconnect with no neutral required but i understand that as long as is cable,permanently marked with like phase marker we should be good ? 200.7
You should be careful about taking advice from whoever told you that.
As Infinity said, the correct term would be re-identify.
 